fuck a duck, i found it. here's the link, although not sure if you can view it if you're not logged into the website? anything you wanna know just gimme a shout though. for some reason, on this particular datasheet, they haven't listed the loading specs for 600watt sodiums, they're not commonly used in industry, there is actually a full datasheet for these contactors that list pretty much every light concievable, but fucked if i can find it now? either way this will suffice, just treat a 600w as a 1000w (always overcompensate with electrics!) also you should be looking at the table for "high pressure sodium vapour lamp (with parrallel connection)" the parrallel connection refers to the capacitor, the fact that with these contactors you can actually have MORE lamps due to the capacitor shows how good they are, because they are limited by the inductive arc, rather than the capacitive inrush, which is the case with most contactors. capacitive inrush is what welds timers on, inductive arcing burns contacts out, so your light wont switch on, and we all know what is usually the case with timers and HID lights
just in case the pdf wont load:
Type of lighting application
230 V single-phase circuit
Maximum number of lamps for a given rating
CT contactors
Power (W) 16 A 25 A 40 A 63 A 100 A High pressure sodium vapour lamp (with parallel correction)
70 6 9 18 25
150 6 9 18 25
250 2 3 6 9
400 2 4 8 12
1000 1 2 4 6
the number on the furthest left, is the wattage of your lamp, the numbers to the right of this are the number of lamps you can have on the contactor, for each of the nominal current ratings. i.e. if you have a 16A Multi9 ct you can have 1 1000w lamps running from it, if you have 2 1000w lamps, you will need a 25A contactor, 4 x 1000watt lamps you will need a 40A contactor, etc
http://www.global-download.schneider-elect...20%28web%29.pdf