Laying a Cable underground
#1
Posted 07 April 2012 - 03:34 PM
I need to know about the size of cable needed and how its best layed, my current plan is to stick a flexible conduit in a 2 foot trench then pull the cable through with a rope.
I will be running probably 3x600w lights plus fans and heaters, then i would also like to run (not all at once) a lathe, bench drill, compressor, small welder, lights, radio and kettle that kinda stuff.
So any advice welcomed I was thinking of running a 2 core 10mm2 swa.
#2
Posted 07 April 2012 - 05:20 PM
The_Moog, on 07 April 2012 - 03:34 PM, said:
I need to know about the size of cable needed and how its best layed, my current plan is to stick a flexible conduit in a 2 foot trench then pull the cable through with a rope.
I will be running probably 3x600w lights plus fans and heaters, then i would also like to run (not all at once) a lathe, bench drill, compressor, small welder, lights, radio and kettle that kinda stuff.
So any advice welcomed I was thinking of running a 2 core 10mm2 swa.
I reckon you'd need 6mm cable for that mate. i wouldn't bother with conduit, just get armoured cable and slap it in. But if you are doing it proper, then be aware of the regs which have criteria regards who is allowed to lay it, and how you run it and mark it up etc.
Best of luck!
All of this will happen again
#3
Posted 07 April 2012 - 05:21 PM
I would use a 16mm SWA as its 100 metres and get a 3 core, internal earth and all that, it sounds like you know what your doing though so good luck
Quote
6mm is only good up to 30 amps (ish) and then thats for relatively short runs which means its 10mm minimum 16mm is a better job
This post has been edited by Davey Jones: 07 April 2012 - 05:23 PM
Reboot universe Y/N_
Trouble rather the Lion in his lair, than the Sage amongst his books.
#4
Posted 07 April 2012 - 06:07 PM
Ill probably go for the 16mm in that case, not cheap though. I must admit to being a bit unsure about the earth, Ive only ever seen the swa used as the earth but those were short 10-15 metre runs.
#5
Posted 07 April 2012 - 08:20 PM
The_Moog, on 07 April 2012 - 06:07 PM, said:
The armouring is perfectly adequate as the earth (up to very large cables) but IMO a separate earth is better especially for a DIY job but it is more expensive so its entirely up to you both ways are fine
If cost is an issue then its best to work out exactly what load you will draw and then you can install the minimum breaker and cable for your requirements
This post has been edited by Davey Jones: 07 April 2012 - 08:20 PM
Reboot universe Y/N_
Trouble rather the Lion in his lair, than the Sage amongst his books.
#6
Posted 13 May 2012 - 04:53 PM
Required Cable Size 16 mm
Voltage Drop 10.9 Volts.
Percentage Drop 4.7%
Current Load 43.0 Amps
Max Cable Load* 46.7 Amps
If your main fuse board is bs 3036 (rewirables) it's gonna be difficult to get a 50-63 amp fuse wire for this. Bare in mine that outside power requires rcd protection. I'd make sure that your fuse board is current with 17th edition. I charge £250-350 for fuse board renews just to give you an idea of what to expect. They may insist the bonding to the water/gas meters be upgraded also, so this might push up the price. If you have a modern fuse board with rcd protection bs 60898 (modern switch fuses) fuses in the 50-63 amp range are easy to pick up. You'd obviously need to fit another comsumer unit in the workshop. This should also have rcd protection to help with any problems tripping the main board in the house.
#7
Posted 13 May 2012 - 05:30 PM
Quote
Why?theres no requirment in the 17Th to bring existingg installations up to standard ,just note it in the inspection and test ticket.As for earthing i wouldnt run an earth ,instead id put a local earth rod in,making it a TT supply,that way you dont have to worry about extending the equipotential zone,and the rules covering TN-C-S systems.
#8
Posted 13 May 2012 - 08:30 PM
#9
Posted 15 May 2012 - 08:26 PM
#10
Posted 18 May 2012 - 06:09 AM
#11
Posted 18 May 2012 - 08:40 PM
Quote
no it dosnt,it comes down to the incoming supply arrangments
#12
Posted 27 May 2012 - 01:05 PM
#13
Posted 27 May 2012 - 01:27 PM
Quote
in this case id say its definatley needed.On any of the lables does it mention pme or protective muliple earthing? Thats the important part on deciding how to install your external supplys
#14
Posted 27 May 2012 - 03:08 PM